For Abacus we have reserved a dedicated 63A connection, this can be used
fully, so 44kW available.
For Battery and Clairvoyance we have a 32A dedicated connection, 22kW
available in each tent.
If needed we can run one or two 16A/230V Schuko extension cords to those
two tents too.
More is not really available due to limitations of scouting infra, but
since we calculated 10kW per tent during normal use it should suffice
even without the extra Schuko.
We didn't plan any distribution infra inside these tents, just the cable
to them. With the exception of the emergency lighting above the exits.
Did I remember this correctly?
--